Rdar43
Structural
- Apr 25, 2022
- 19
I have a condition where a gauge metal studs were fabricated with noncircular knockouts that have 9" of material at the end of the studs. In AISI S100-16 1.1.1 it indicates provisions for the modification of effective width of studs with knockouts but is only applicable when the end distance is 10". The section also indicates that the effective width can be determined with a stub-column test but I'm wondering if there is an alternative analysis for this condition. Since the studs are close to the requirement I'm leaning towards telling the G.C. to apply web stiffeners at every location and moving on but not sure if there are any other suggestions.
Thanks,
Thanks,