Lion06
- Nov 17, 2006
- 4,238
I have a question regarding FMC frames and how you calc the effective length factors, K.
When doing a sway frame building using FMC for the lateral system, you are almost required to use the nomograph to calc the K factors. The reason being that you can't simply use any of the idealized cases shown in the AISC Manual for several reasons. First, because of the FMC you will never have an idealized fixed connection at the top of the column at the first floor or at either end of columns above that. For the lowest column level the only other option at the top is to have it free (to use the recommended K values). The top of the column cannot be assumed free, because the base is not fixed. While it may be fixed for wind moment only, I don't believe that the footing/base plate/anchor bolts designed based on the wind moment only will provide a rigid enough base to assume this is fixed.
Now you have a Gtop moving up due to the decreasing stiffness of the connecting beams (in addition to only being able to include (1) of the girders in Gtop instead of both), and a Gbottom moving up due to the decreased stiffness of the footing/BP/AB assembly.
These things add up and can significantly increase the K you would get if you assumed fixed connnections everywhere.
I have read a few papers on this and most reference using the moment-rotation curve for the connections to get the stiffness and use that in the G calcs. That is all well and good, but part of the beauty of the FMC is its economy. The economy goes away if you have to test the connections - especially if you have 10 different connection types on a building.
One paper, by Geschwindner, talks about the moment-rotation of the connection to lay the groundwork for his method, but I don't completely agree with it. He only uses (1) of the connecting girders (which I agree with), he also doubles the length of that (1) girder (to account for the far end of that girder being pinned (since the connection has reached its plastic moment capacity and is being loaded, but cannot resist any more moment), but makes no allowance for the connection being less stiff than the beam (this is the part I disagree with).
Does anyone have a method for calculating a K factor under these conditions or know of a good paper to read?
I am really trying to understand what is going on so I can come up with a method to accurately model this in RAM.
RAM has a procedure for this type of building, but I don't completely agree with it. They say to design gravity first (fine), the fix the beams and run lateral only and make sure the beams are ok (fine). Then run lateral and gravity, only sending 10% DL moment to columns with lateral loads - the problem with this step is that there are only two options for K - either RAM calcs it using the nomograph or you input it. You obviously can't input a single K for every column unless you are being VERY conservative, which again takes away from the economy of the system, but if you use the nomograph it calcs K as if the connections are fixed, which is UNconservative.
Does anyone have any suggestions?