The software that we use for structural steel analysis, (Tekla TEDDS), will in some cases result in adequate column strength in shear strength, compressive strength, flexural strength, and combined forces. However, it issues the warning that "member slenderness exceeds 200". (In this particular case the KL/r = 210). Reading the AISC steel manual 13th edition, with regard to column slenderness, "KL/r should preferably be limited to a maximum of 200". Then "Note that this recommendation does not apply to members that are primarily tension members..."
When they use words like "recommendation" and "preferably" I think that it's okay to exceed 200. But would it be considered inadequate?
If it was only a single column being considered I'd just upgrade the column so the preference is satisfied. But there are numerous columns for this project, and there's some motivation to make the column sizes the same for fabrication and construction simplicity. And I don't want to upgrade all 20 for the one outlier.
Thanks for your input.
When they use words like "recommendation" and "preferably" I think that it's okay to exceed 200. But would it be considered inadequate?
If it was only a single column being considered I'd just upgrade the column so the preference is satisfied. But there are numerous columns for this project, and there's some motivation to make the column sizes the same for fabrication and construction simplicity. And I don't want to upgrade all 20 for the one outlier.