columns stirrups extending inside horizontal element

Status
Not open for further replies.
Replies continue below

Recommended for you

Yes, in non seismic areas, column ties are not normally placed within the horizontal member depth.
 
2" or 3" above slab surface and 2" or 3" below slab soffit. Spacing as required in-between, usually 12". Nothing in slab thickness as long, assuming it's not an unusually large depth.
 