omoreno1
Structural
- Nov 6, 2007
- 14
I have a rather unique situation. Table 2508.5 note a of the 2006 IBC indicates that gypsum board horizontal diaphragms are not cummulative with wood structural panels. IBC section 2305.3.9 exception allows the summation of wood structural panel and gypsum wall board in shear wall members to be additive (this is for accounted in APA examples). I have an engineer who is indicating to me that IBC provisions under shearwalls are also applicable to roof diphragms in this scenario. I have done extensive research in the building code, APA, AFPA, and wood design textbooks and cannot find a single example combining these two capacities linearly in the case of roof diaphragms. Does anyone have any idea how this may be approached. I realize gypsum is a much stiffer material than plywood and an appropiate analysis would include testing or a FEM model with the relative stiffness of each material and the roof truss assembly. I realize the assembly may have more stiffness, but i cannot see a linear correlation with strength. Can anyone enlighten me on what I am missing here?