RFreund

Structural
Aug 14, 2010
1,881
Does anyone know of any information for combining different fastener strengths. Such as nails with bolts or any other combination for that matter?

EIT
 
Replies continue below

Recommended for you

I would think for wood it would be relatively additive. I would be providing the largest spacing between the unlike fasteners (likely governed by bolts).
 
By CWC they are additive. The controlling failure for nails in anything softer than D.F. is usually lateral deformation of the nail, while in bolts it is usually yielding of the wood itself.

I would think a prudent design would to find the maximum capacity of your nails first, and then size an appropriate bolting connection to take up the rest as the nails will usually fail first.
 
I'm living up to this one... I may have lied - I was thinking of a Simpson whitepaper on multiple fasteners but it was not CWC or CSA approved - truly sorry about that. Will fact check more thoroughly before I post in the future.

OS86 - 10.2.2.3.1 & 10.2.2.3.2: "... fastenings of the same type and size arranged symmetrically..."
 
I would not use both unless the bolts could be installed first, then loaded to take up the hole slop, then the nails installed. (Like that's going to happen). Otherwise the nails could take all the load until they fail if there is too much play in the bolt holes.

Mike McCann, PE, SE (WA)


 
@Signious - no worries.

@msquared - Good points.

This is evaluating an existing condition that has been there for a long while. If designing new I would not combine them. For my situation even combining the nails and bolts did not meet the required strength, so I will need to reinforce the connection ("but at has stood for years!" they will shout I'm sure). I was curious for future reference.