Common venting of mutiple clothes dryers? 1

Status
Not open for further replies.

tlae

Structural
Feb 17, 2003
4
Any experience with this? I would like to use a common in-line fan with w/ pressure or heat sensor at each dryer for control. Individual vents would also be equiped with a cape backdraft damper. This is for a multi-family project, converting an old concrete hotel, mech'l contractor suggesting the change from individual runs to minimize core drilling. Fundementally, I do not see why this would not be effective but but I have no practical experience to justify.

Thanks for any comments.
 
Replies continue below

Recommended for you

GE has design guidelines for common vent risers. Go to their website and search for dryer venting guide. There a design for fan-assisted and non-fan assited. I would use the latter and provide a a lint clean-out hatch at the base of the riser.
 