Agent Coconut
- Dec 27, 2024
- 6
Hi everyone,
I was assigned as designer engineer for a new project recently and this is my first time to lead on a project.
While the analysis of building frame is not a trouble for me, I have several questions on the detailing part.
As for the background, in my region most of the structural consultant including my seniors are still adopting the old BS8110:1997 but while local authority has requested us to use EN1992, but they have not enforce this yet and even accepted and approved our engineering design submission including calculation that was still adopting BS8110. Even worse, our clients are aware of this phenomenon. The issue is, I am intend to adopt EN1992 for the new and future project but I was questioned by many engineer of my field including my seniors therefore I am looking for clarification from everyone here who is not from my region and was hoping that I can some new insight.
My clients and my seniors is in opinion that BS8110 will give a cheaper structural solution and better flexibility as compared to EN1992 despite EC2 allow a lower load factor based on the following argument.
1) Anchorage and lapping length of reinforced concrete element.
We all know that the lbd and l0 length for Eurocode 2 is much longer than BS8110 and even was acknowledged from concretecenter
The client and my senior are in opinion that since most of our project is adopting lower concrete grade (C20/25 or C25/30), the will incur a lot of additional cost if we adopt EN1992.
For example: a H12 bar will need to lap for a total of 56d at poor zone but 87d for EC2
2) Additional tensile reinforcement due to shear
These tensile force due to shear is not presented/required when using B8110, thus, with this new detailing rules, the bottom reinforcement at support are more than what is required when it is based on BS8110, especially when we are analyzing a high rise where lateral load is significant and beams are now acting as tie beam, thus no longer behave as normal moment and shear force diagram that we always know in some critical load case.
3) Deflection of band beam/conceal beam
In BS8110, the deflection using l/d is straightforward but in EC2 and if we adopt UK NA (we foresee our regions will follow the recommendation from UK NA based on past experience) it is limited to 40K, this has made conceal beam concept most likely cannot be adopted due to deflection by mean of l/d is not being satisfied, which on paper, BS8110 can made this beam happened, and become a preference for our clients.
Anyone can enlighten me on the technical background that lead to these changes and more importantly, any technical explanation to explain and to clarify all these so that I can explain to my client, who obviously prefer a cheap solution rather a robust and modern design practice?
Apologize for the long post and thank you everyone for your time.