Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Composite column - Fire protection 2 hours - Big diameter D=900mm

Status
Not open for further replies.

daranguiz

Structural
Aug 19, 2016
24
Hello,

I have a composite column CHS900x40 that needs to be protected for 2 hours.
The calculation method exposed on Eurocode is not applicable for columns with D>400mm. The solution proposed by the EC is either protect the steel for T=350°C or do a thermal calculation (fancy software). I've been told by some fire experts that the behavior of a composite column under fire is such as the increase in the steel is slower and maybe won't activate the chemical reaction when needed on the intumescent paint.

Do you know an intumescent paint for composite columns that is able protect for 350°C?
Does AISC or other codes give some guidance on this subject?

Thank you very much
 
Replies continue below

Recommended for you

Well, I talked to 2 fire design experts and I learned 2 things:

- It's unsafe to calculate the resistance of the column under fire by ignoring the concrete. Because the loads under fire are less important, I though than maybe I could check for steel only, but it's an unsafe approach because of "the unequal temperature field creates a rather inhomogenous distribution" and "the unequal temperature field leads to strong internal stresses" ( see Technical note #55 of ECCS)

- In eurocode, for big columns (diameter>400mm) I have to check with a lab or run a thermal calculation
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor