Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

composite steel beam design - lateral restraint of beams - fire protection of steel beams

Status
Not open for further replies.

JohnnySm

Structural
Feb 2, 2017
19
GB
Dear All.

5 storey steel frame building (residential). Steel beam with steel/concrete deck flooring kingspan or something.

1. is it sufficient to assume that if the decking trays are positioned and cut correctly, so as to ensure a trough of the deck lies on the top flange, can beams running parallel to the span of the decking be assumed laterally restrained with the use of designed shear studs? i know this is the case with beams spanning perpendicularly.

2. The beams are not designed for composite action but have been designed for full lateral restraint only FYI.

3. in terms of fire protection i know a lot of fabricators assume top flanges of steels where shear studs are located should arrive on site unprotected? is this because they assume i have designed for composite action between the slab and bean? i have not... furthermore with trapazoidal decking this leaves approximately 50% of the top and untreated flange exposed after installtion? should i request these voids to be filled in on site? this seems like something i think the site workers would want to avoid? is it not more preferable to just have the steels fully protected during fabrication? or does this conflict the shear stud installation process? is it standard to request voids filled in on site?

Kinest Regards
JS
 
Replies continue below

Recommended for you

I don't consider composite steel beams to be laterally braced while the concrete is wet if the steel deck is parallel to the beam. I feel like the decking would, at best, act like an accordion and not provide lateral restraint of the top flange. Most engineers I know agree with this.

You could reach out to the decking manufacturer and ask if they have any test data that proves otherwise, though.
 
Status
Not open for further replies.
Back
Top