Compressive strength of existing concrete walls
kaffy
191
Good Morning guys,
How do you determine the compressive strength of existing concrete walls / concrete floor if no structural drawings or any technical data is available? Are there any code requirements stating that minimum compressive strength of concrete allowed? I need to specify the anchor bolts but since I do not know the compressive strength, how should I proceed?
So you're just looking for f'c, right? If the concrete is in good shape then you can probably assume 2500psi (about 17 MPa if my conversion is correct) conservatively. If it's a critical application (failure could cause serious injury or death or significant property damage), then I'd insist on having a testing lab core few samples to test it if you need anything more than that.
Yes f'c. Thank you very much
I would tend to agree with pham on the 17 MPa being a good lower bound. When was the original structure built? I haven't seen any concrete strengths lower than 25 MPa going back a lot of years here in Canada.
Even when specifying 20 MPa grout for CMU walls we end up above 25 MPa on 99% of it. And that's cylinder results, the in-situ strength is likely significantly higher due to the moisture being sucked out of the mix by the block.
It was built in 1972.I see. Thank You very much