I've got a client that wants to bear a new steel beam on an old brick wall...just to support a new folding partition.
The loads are small. I've calculated them to be about 2.7 kips when the panel is all folded up at one end.
What do you guys use for the allowable compressive strength of masonry on an old brick wall such as this?
Just to check, I calculated a short length of wall, 8" thick, and about 9'-0" tall for buckling under load, but am unsure about the allowable compressive strength I should use in the calculation.
The smallest value I see in table 5.4.2 of ACI 530 is about 100 psi. I was thinking of using this small value, times the buckling calc of about 0.22, and I get about 22psi allowable.....when spread over about 2'-8" length of wall, I only have about 11psi actual....which seems ok.
Any opinions?