In the context of designing a jetty exposed to severe marine conditions (exposure class XS3), I am considering a concrete mix design that meets the structural requirements and prioritises environmental sustainability. Having identified a concrete grade of C40 with a water-cement ratio between 0.35 and 0.4 as a potential fit, I seek recommendations on the most suitable cement mix or standards that address this. Will be interesting to hear your ideas. Thank you
 
Replies continue below

Recommended for you

XS3 and C40 sounds like you're using European code. It has been a while since I have used them. But values around C40 are typically design mixed and not the responsibility of the design engineer. Admixtures and higher-grade cementitious materials are used so I can't give an exact mix ratio.

For your structure, you should consider adequate concrete and size for durability. I believe EC2 covers that part
 
In Canada, you can spec a concrete mix design or leave this option up to the suppler. Typical spec options are: type of construction, f'c, cement type, max w:c, max slump, aggregate size, air content, and admixtures. For your use:
[ul]
[li]I would assume the C40 is 40MPa;[/li]
[li]you would specify the type of cement powder to be used depending on the requirement (this can be left to the supplier);[/li]
[li]you can set the w:c to 0.4 max;[/li]
[li]you can set the slump equal to 75 to 100 max, depending on what you are doing;[/li]
[li]max aggregate size can be set to 40mm, or larger if you can use it;[/li]
[li]air content can be set to 5% to 7%, depending on what you are doing; and[/li]
[li]admixtures can include the normal ones plus you can add a hydrophobic one to reduce the permeability.[/li]
[/ul]

In addition:
[ul]
[li]you have to take care of any rebar coating systems;[/li]
[li]make sure you have adequate concrete cover;[/li]
[li]you need sufficient bar spacing to reduce cracking; and[/li]
[li]make sure you have adequate consolidation for a dense cocrete placement.[/li]
[/ul]

We would normally leave the mix design to the supplier. The supplier should provide you with their mix design so you can review it (or have a good geotekkie review. Suppliers are often reluctant to provide this because they consider it proprietary. Have this as a specification requirement).


-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 