Hi
I would really appreciate some assistance to confirm some fundamentals and sort out some nagging uncertainties that I have with respect to concrete compression members.
Firstly, I tend to define a column as a compression member that utilizes compression reinforcement and a wall as a compression member that doesn’t.
Columns
It is my understanding that a column subject to a load takes the force in the concrete and steel with stresses in each proportionate to the modular ratios. Creep and shrinkage further reduce the stress in the concrete and increase it in the steel.
Q – Given that all column calculations include the vertical reinforcing how are situations/zones where the reinforcing is not developed handled? I am referring to column connection situations where either:
- A compression splice is not provided with the starters (vertical column bars not developed in compression until about 20db).
- Less starters bars (diameter, number etc.) than the vertical reinforcing are provided or the starters are not developed in compression themselves (reduced fy) or are in a different position (which they have to be) than the design cross section.
- Negligible connections (shear dowels, precast connections) etc are provided.
Given the requirement for developed (in compression) reinforcing it seems that the critical cross section (and therefore the design cross section) should be taken at the top or the base of the column (<20db) for all columns that don’t have fully developed starter bars providing compression splices with all of the vertical reinforcing. The design cross section for the most extreme situation (shear dowels) is effectively an ‘unreinforced’ cross section (a wall?).
It seems possible that higher bearing stresses could be permitted at these local end zones, but I cannot find any justification or design methodology for addressing the stated situations. Help?
Walls
Despite walls tending to have a much lower reinforcing ratios than columns they still carry load in the exact same fashion as columns (ie stresses proportionate to modular ratios etc..) . I am therefore confused by the arbitrary restraint requirements for the vertical reinforcing. AS3600, CL 11.6.4 requires restraint for walls ‘designed as columns’ when N*<0.5phiNu. I design my walls, and most of the time my wall end zones as walls, not as columns (what a sentence!). I still end up with situations (tension loads, wind loads, lifting in precast) where walls end up with a very high percentage of steel – not for compression.
I assume that chapter 11 has been written on the basis that a given cross section cannot be loaded such that the stress in the steel exceeds the buckling stress (anyone know what that is?) and restraint for the vertical reinforcing is therefore not required.
Q- How can the above assumption be justified without a specified maximum reinforcing ratio? Isn’t it possible for heavily reinforced (not for compression) walls have the bars buckle and spall? Or is the fact that the bars are not heavily loaded (below the buckling stress) eliminate this problem? (Note that the draft code waives restraint requirements for walls ‘designed as columns’ for either - N*<0.5phiNu, concrete strength is <50MPa and vertical reo is not used in compression, % reo is not greater than 0.02 with min horiz of 0.0025).
I have had (precast) walls that have been designed close to their limit as walls that have ended up with close 0.01 of steel in them due to lifting requirements trimmers etc.. I ended up specifying ties (not quite complying with Cl 10.7.3.1 ‘to every alternate bar’) just because it ‘didn’t look right’…
Q- Are reinforced shear walls subject to the slenderness beam limits (Cl 8.9) as they are ‘cantilevering deep beams’?
Q- Is a reduced design cross section required for precast walls with chamfers (say 20x20) at the ends>
Thanks in advance for your time! It is much appreciated.
I would really appreciate some assistance to confirm some fundamentals and sort out some nagging uncertainties that I have with respect to concrete compression members.
Firstly, I tend to define a column as a compression member that utilizes compression reinforcement and a wall as a compression member that doesn’t.
Columns
It is my understanding that a column subject to a load takes the force in the concrete and steel with stresses in each proportionate to the modular ratios. Creep and shrinkage further reduce the stress in the concrete and increase it in the steel.
Q – Given that all column calculations include the vertical reinforcing how are situations/zones where the reinforcing is not developed handled? I am referring to column connection situations where either:
- A compression splice is not provided with the starters (vertical column bars not developed in compression until about 20db).
- Less starters bars (diameter, number etc.) than the vertical reinforcing are provided or the starters are not developed in compression themselves (reduced fy) or are in a different position (which they have to be) than the design cross section.
- Negligible connections (shear dowels, precast connections) etc are provided.
Given the requirement for developed (in compression) reinforcing it seems that the critical cross section (and therefore the design cross section) should be taken at the top or the base of the column (<20db) for all columns that don’t have fully developed starter bars providing compression splices with all of the vertical reinforcing. The design cross section for the most extreme situation (shear dowels) is effectively an ‘unreinforced’ cross section (a wall?).
It seems possible that higher bearing stresses could be permitted at these local end zones, but I cannot find any justification or design methodology for addressing the stated situations. Help?
Walls
Despite walls tending to have a much lower reinforcing ratios than columns they still carry load in the exact same fashion as columns (ie stresses proportionate to modular ratios etc..) . I am therefore confused by the arbitrary restraint requirements for the vertical reinforcing. AS3600, CL 11.6.4 requires restraint for walls ‘designed as columns’ when N*<0.5phiNu. I design my walls, and most of the time my wall end zones as walls, not as columns (what a sentence!). I still end up with situations (tension loads, wind loads, lifting in precast) where walls end up with a very high percentage of steel – not for compression.
I assume that chapter 11 has been written on the basis that a given cross section cannot be loaded such that the stress in the steel exceeds the buckling stress (anyone know what that is?) and restraint for the vertical reinforcing is therefore not required.
Q- How can the above assumption be justified without a specified maximum reinforcing ratio? Isn’t it possible for heavily reinforced (not for compression) walls have the bars buckle and spall? Or is the fact that the bars are not heavily loaded (below the buckling stress) eliminate this problem? (Note that the draft code waives restraint requirements for walls ‘designed as columns’ for either - N*<0.5phiNu, concrete strength is <50MPa and vertical reo is not used in compression, % reo is not greater than 0.02 with min horiz of 0.0025).
I have had (precast) walls that have been designed close to their limit as walls that have ended up with close 0.01 of steel in them due to lifting requirements trimmers etc.. I ended up specifying ties (not quite complying with Cl 10.7.3.1 ‘to every alternate bar’) just because it ‘didn’t look right’…
Q- Are reinforced shear walls subject to the slenderness beam limits (Cl 8.9) as they are ‘cantilevering deep beams’?
Q- Is a reduced design cross section required for precast walls with chamfers (say 20x20) at the ends>
Thanks in advance for your time! It is much appreciated.