I've gone through a bunch of messages on the site regarding concrete cover to bottom reinforcing.
The reasons given for increasing cover are:
-irregularity of soil surface,
-intrusion of granular base material into slab,
-the possible loss of water to the granular base, having undesirable effects, and
-the contact with a 'wetted' soil will cause the concrete to be saturated.
My comments on the above reasons:
I've not encountered irregularities of the soil; it's usually compacted smooth,
The PEVB prevents intrusion of the granular base into the concrete, and,
The concrete cover to the side allows water into the hardened concrete, so, the 3" clear cover with 1-1/2" side cover serves no purpose for moisture.
I had a recent project where the owner cast a 2' thick slab on grade (to keep weeds down) and then constructed a deck over it. Some of the supports were on screw piles that were sleeved so that there was no load applied. Some of the supports were on the 2' thick slab. Getting the maximum plain concrete moment resistance, I used the full thickness of the slab since there was a PEVB between the slab and fill. Canadian codes require that you ignore the bottom 2" if cast against soil. I chose not to.
I've another project where the excessive bottom cover is posing problems with exposure crack widths. The grade beam will be cast on 'foam void form'. I'm planning to use 2" cover which works for exterior exposure, and, was thinking that 1-1/2" (similar to the sides) could be appropriate.
Any comments would be appreciated...
Dik
The reasons given for increasing cover are:
-irregularity of soil surface,
-intrusion of granular base material into slab,
-the possible loss of water to the granular base, having undesirable effects, and
-the contact with a 'wetted' soil will cause the concrete to be saturated.
My comments on the above reasons:
I've not encountered irregularities of the soil; it's usually compacted smooth,
The PEVB prevents intrusion of the granular base into the concrete, and,
The concrete cover to the side allows water into the hardened concrete, so, the 3" clear cover with 1-1/2" side cover serves no purpose for moisture.
I had a recent project where the owner cast a 2' thick slab on grade (to keep weeds down) and then constructed a deck over it. Some of the supports were on screw piles that were sleeved so that there was no load applied. Some of the supports were on the 2' thick slab. Getting the maximum plain concrete moment resistance, I used the full thickness of the slab since there was a PEVB between the slab and fill. Canadian codes require that you ignore the bottom 2" if cast against soil. I chose not to.
I've another project where the excessive bottom cover is posing problems with exposure crack widths. The grade beam will be cast on 'foam void form'. I'm planning to use 2" cover which works for exterior exposure, and, was thinking that 1-1/2" (similar to the sides) could be appropriate.
Any comments would be appreciated...
Dik