The Situation
- Solid precast plank as shown below. Heavy transfer slab loads.
- Normally a one way spanning thing but, at the supports, the thing has to span laterally over some louver openings that extend to the underside of the slab.
- Local gaggle of rebar placed in the ends of the plank to serve as lateral beams of sorts (tiny spans).
The Question
Good detailing practice, as I know it, would have the bottom bars of the supported slab run up over the bottom bars of the supporting "beam". That, so that there is no potential crack such as the one shown in green that does not intercept any reinforcing. I might accomplish such a thing in several ways:
1) Drape the slab rebar.
2) Lap the rebar with an offset piece that comes up and over the beam bottom bars, a bit like a 1:6 column rebar transition.
3) Simply adjust the layering and take the hit with respect to slab flexural depth and crack control.
I could do these thing but the question is this: do I need to? All of the proposals above would be a bit annoying to my precast client for various reasons.
Some Related Logic
4) For a more discrete, serious beam & girder situation, I would definitely do this.
5) In a way, a similar condition exists everywhere within a two way slab and we do not do this.
6) So is this closer to a serious beam situation or closer to a two way slab situation? My gut feel is that it is the latter and I'm inclined to not worry about this here.
- Solid precast plank as shown below. Heavy transfer slab loads.
- Normally a one way spanning thing but, at the supports, the thing has to span laterally over some louver openings that extend to the underside of the slab.
- Local gaggle of rebar placed in the ends of the plank to serve as lateral beams of sorts (tiny spans).
The Question
Good detailing practice, as I know it, would have the bottom bars of the supported slab run up over the bottom bars of the supporting "beam". That, so that there is no potential crack such as the one shown in green that does not intercept any reinforcing. I might accomplish such a thing in several ways:
1) Drape the slab rebar.
2) Lap the rebar with an offset piece that comes up and over the beam bottom bars, a bit like a 1:6 column rebar transition.
3) Simply adjust the layering and take the hit with respect to slab flexural depth and crack control.
I could do these thing but the question is this: do I need to? All of the proposals above would be a bit annoying to my precast client for various reasons.
Some Related Logic
4) For a more discrete, serious beam & girder situation, I would definitely do this.
5) In a way, a similar condition exists everywhere within a two way slab and we do not do this.
6) So is this closer to a serious beam situation or closer to a two way slab situation? My gut feel is that it is the latter and I'm inclined to not worry about this here.