Concrete Intersecting Beams Joint ->Cold or not?

Status
Not open for further replies.

structurebeton

Structural
Apr 24, 2003
88
Hello,
I would like your advise on this problem:
One RC beam perpendicular to another, same level, one acts as a support for the other. Does the joint needs to be constructed as a monolothical pour? What happens if poured separately? Does longitudinal rebar sticking out into other beam sufficient to take shear? Let me know what you think. Thanks.
 
Replies continue below

Recommended for you

Normally you try very hard to avoid any cold joints in this region near intersecting beams. In fact, we usually require the contractor to lay out all his planned construction joints and submit them for approval. We specify that the joints should cross only areas within the middle third of any span.

If for some reason you cannot achieve this, then a cold joint at an intersection can be dealt with. You simply have a shear friction situation and your reinforcing, above and beyond what is needed for flexure, must be added across the joint to satisfy the shear friction capacity. The joint should be keyed or otherwise intentionally roughened.

See Chapter 11 in the ACI code under Shear Friction for the method.

But I would avoid the situation if you can.
 