jjezmarlo3
Structural
- Aug 9, 2012
- 13
This is for all of you WWTP designers out there. What mix design have you been using for Headworks structures, or other structures with relatively high exposure to sulfates? We have generally been using the same mix design we use for all watertight structures (f'c = 4,500 psi, w/c = 0.42, Type II cement, 6% air) as recommended by ACI350-06 Table 4.3.1 for 'moderate' sulfate exposure, and then recommending the Headworks be lined with a protective coating. But I'm wondering if it might be beneficial to jump to the 'severe' sulfate design mix for the headworks (f'c = 5,000 psi, w/c = 0.40, Type V cement, 6% air) instead. My only concern here is that for some of the small municipalities, Type V cement might be hard to come across. Any thoughts?