Bridge100
- May 3, 2007
- 24
Could somebody please direct me to a good concrete formwork publication or help me with the following problem? I’m designing formwork for an inclined concrete column but I can’t find anything that deals with this problem. The contractor would like to pour the entire 40 Ft tall column in one day.
Looking at the design of the underside incline bulkhead I am considering the following:
All vertical and lateral loads must be converted to force components normal to the forming face. (See attached method B)
The shear components of the vertical and lateral loads will not be resisted by the form since the form does not have shear connectors or friction with the fluid concrete (See attached method A). Therefore, the shear component of the vertical concrete load will travel through the previously cast pier stem below.
The lateral load would be based on an assumed allowable form pressure. I know that ACI 347 suggests designing for full liquid head for columns this tall; however, it has been the contractor’s experience to use penetrating rods to determine when initial concrete set has occurred.
The vertical normal component would vary from zero at the top of the form to 150pcf*40’*cos2(A) at the bottom.
The lateral normal component would be a uniform load of 150pcf*Liquid Head (Ft)*sin2(A).
Can anybody see problems with this approach?