boffintech
Civil/Environmental
- Jul 29, 2005
- 469
The particulars:
1. parking deck elevated slab 9” thick with 5” drop panels
2. columns F’c = 10,000psi
3. slab F’c = 5,000psi
4. actually placing concrete F’c = 7,000psi to eliminate puddling 10ksi column mix at column heads during slab placements
5. five levels of parking deck are below street level
6. a permanent shotcrete foundation wall borders 3 sides of the below street level slabs
7. the slabs will be tied to the fdn wall with #4s @ 12” crossing a 3’ wide pour strip and having a 2’ splice
8. the specs read to not place concrete for the pour strips until 28 days after the PT is stressed.
The question:
The 7ksi slab mix is high-early type III which rockets to 4500psi in 24 hours. By 7 days the breaks are >6,500psi. The 24 hour breaks are super accurate; I’m using Command System and 6x12 cylinders kept at similar temps.
Considering that the PT is stressed the day following the placement and considering the rate at which the concrete gains strength is there any reason to wait beyond 7 days to place concrete for the pour strips?
More shrinkage? Equilibrium?
1. parking deck elevated slab 9” thick with 5” drop panels
2. columns F’c = 10,000psi
3. slab F’c = 5,000psi
4. actually placing concrete F’c = 7,000psi to eliminate puddling 10ksi column mix at column heads during slab placements
5. five levels of parking deck are below street level
6. a permanent shotcrete foundation wall borders 3 sides of the below street level slabs
7. the slabs will be tied to the fdn wall with #4s @ 12” crossing a 3’ wide pour strip and having a 2’ splice
8. the specs read to not place concrete for the pour strips until 28 days after the PT is stressed.
The question:
The 7ksi slab mix is high-early type III which rockets to 4500psi in 24 hours. By 7 days the breaks are >6,500psi. The 24 hour breaks are super accurate; I’m using Command System and 6x12 cylinders kept at similar temps.
Considering that the PT is stressed the day following the placement and considering the rate at which the concrete gains strength is there any reason to wait beyond 7 days to place concrete for the pour strips?
More shrinkage? Equilibrium?