i've thumbed through a few threads that mention initial cure of concrete specimens/cylinders. i occassionally run across jobs where low breaks show up and the contractor tries to blame the testing firm for the low break since there is no storage box on site. unless the specifications or client specifically direct me to provide a storage box on site, it falls back on the contractor to provide such a box since they are responsible for their site, storage of all materials on the site, and protection of the materials on site. and as usual, the supplier and contractor try to throw us "under the bus". the issue is usually resolved because the contractor provides a storage box, they reduce placement times, and they improve onsite handling of the concrete. i have many construction jobs going on very near this site and none of those guys are experiencing the same problem. so i'm interesting in some other opinions on here since i'm sure contractors, suppliers, engineers, testing firms etc visit this site.
i've got a job that has many low breaks. the low breaks are typically within 500psi of the design strength (but too many low breaks to satisfy the aci low break criteria). the passing breaks are all very marginal and usually within 300psi of the design strength. low breaks started showing up at the beginning of the job prior to the temps being high (highs were about 80-85). the contractor said that the low breaks were due to the testing firm not storing the samples properly. i told the project team that we will gladly store the samples where directed at the jobsite and can put them in a storage box once one is provided by the contractor. (if no box is available, we attempt to cover the samples with a box or semi-bury the cylinders to get them out of the sun. we also use plastic bags or plastic tops on the cylinder molds). and on a side note, we learned the first round of low breaks was due to the wrong mix being sent to the jobsite--correct id number on the tickets but the plant had the wrong mix in their system. i have also learned that the particular plant is having difficulties with batching consistency. so, we cored the area at 70 days old and the core breaks were 100-350 psi higher than the design strength. the contractor stated that "we reviewed the break results and all the results are passing therefore the cylinders must be made incorrectly". i tried to be political and said that i reviewed the results and they looked reasonable to me given the age and strength--in other words, i didn't make personal attacks like the contractor is making toward me.
they finally provided a storage box so we've been placing the samples there. the low breaks are continuing with the passing results still marginal. now they're saying that the testing firm is responsible because we're not keeping the initial cure temps regulated (in their storage box). anyone have any thoughts on how to be political about this without calling the contractor an idiot? i have maintained that we cast and test the cylinders in accordance with astm but that we're not responsible for the initial onsite storage conditions since it's not our jobsite. i also noted that aci says that the placement times should be reduced in hot weather but the contractor continues to simply say we're leaving samples in the sun and not following astm (by leaving them in the sun, he means the storage box they provided is in the sun but implies we're leaving the cylinders laying out in the sun).
a little more background: the placement times vary from 1 hour to 2 hours. concrete temps at the time of placement vary from 80-96 degrees. slumps are generally 5-6" range with occasional 8". 7 day breaks are typically about 50-70% of design strength (3000-3500psi) and the 28 days are 85-110% of design strength. 56 day strength are typically only 10% higher than the 28 day strengths. ~70 day old core breaks are typically 101% to 120% of design strength.
a little more background: these guys are very difficult to deal with since during the masonry work, they had never heard of building code requirements and were ready to fight when they were told to cover their materials onsite and to consolidate grout. we have not been extremely picky over the masonry inspections since the architect is pretty lax about the requirements and required inspections. in other words, the contractor is doing his best to be difficult and get back at us because of his own lack of knowledge of the requirements.
any thoughts on the best way to get this settled so that i can get on with work?
i've got a job that has many low breaks. the low breaks are typically within 500psi of the design strength (but too many low breaks to satisfy the aci low break criteria). the passing breaks are all very marginal and usually within 300psi of the design strength. low breaks started showing up at the beginning of the job prior to the temps being high (highs were about 80-85). the contractor said that the low breaks were due to the testing firm not storing the samples properly. i told the project team that we will gladly store the samples where directed at the jobsite and can put them in a storage box once one is provided by the contractor. (if no box is available, we attempt to cover the samples with a box or semi-bury the cylinders to get them out of the sun. we also use plastic bags or plastic tops on the cylinder molds). and on a side note, we learned the first round of low breaks was due to the wrong mix being sent to the jobsite--correct id number on the tickets but the plant had the wrong mix in their system. i have also learned that the particular plant is having difficulties with batching consistency. so, we cored the area at 70 days old and the core breaks were 100-350 psi higher than the design strength. the contractor stated that "we reviewed the break results and all the results are passing therefore the cylinders must be made incorrectly". i tried to be political and said that i reviewed the results and they looked reasonable to me given the age and strength--in other words, i didn't make personal attacks like the contractor is making toward me.
they finally provided a storage box so we've been placing the samples there. the low breaks are continuing with the passing results still marginal. now they're saying that the testing firm is responsible because we're not keeping the initial cure temps regulated (in their storage box). anyone have any thoughts on how to be political about this without calling the contractor an idiot? i have maintained that we cast and test the cylinders in accordance with astm but that we're not responsible for the initial onsite storage conditions since it's not our jobsite. i also noted that aci says that the placement times should be reduced in hot weather but the contractor continues to simply say we're leaving samples in the sun and not following astm (by leaving them in the sun, he means the storage box they provided is in the sun but implies we're leaving the cylinders laying out in the sun).
a little more background: the placement times vary from 1 hour to 2 hours. concrete temps at the time of placement vary from 80-96 degrees. slumps are generally 5-6" range with occasional 8". 7 day breaks are typically about 50-70% of design strength (3000-3500psi) and the 28 days are 85-110% of design strength. 56 day strength are typically only 10% higher than the 28 day strengths. ~70 day old core breaks are typically 101% to 120% of design strength.
a little more background: these guys are very difficult to deal with since during the masonry work, they had never heard of building code requirements and were ready to fight when they were told to cover their materials onsite and to consolidate grout. we have not been extremely picky over the masonry inspections since the architect is pretty lax about the requirements and required inspections. in other words, the contractor is doing his best to be difficult and get back at us because of his own lack of knowledge of the requirements.
any thoughts on the best way to get this settled so that i can get on with work?