Concrete temperature range in hot weather

Status
Not open for further replies.

HOMIeeee

Civil/Environmental
Nov 16, 2016
7
Hey guys
What is the Concrete temperature range in hot weather (C)
What is the maximum time since the ready mix truck leaves the plant
Please i need answers with bsi code or astm
 
Replies continue below

Recommended for you

Refer to ASTM C94.

Temperature will vary depending on many variables, such as....

1. How are the aggregates stored?
2. If open stockpiles, what color are the aggregates (dark or light)
3. What is your location? (Generally cool, warm or hot weather?)
4. What is the mix water temperature?
5. What is the mix design? (higher cement contents in the mix will increase the mix temperature because of increasing heat of hydration)
6. Have you considered ACI's Hot Weather concrete placement recommendations?
7. Is there an available source of cooling for the mixes, such as large quantities of ice to use in lieu of water in the mix or liquid nitrogen cooling in the mixing drum, etc?
8. What is the distance to the jobsite from the batch plant? The longer the distance, the more the temperature will rise.
9. Have you considered using Maturity Methods for checking the curing process of the concrete?

As you can see, there are many, many considerations that have to be made to respond to your overly broad questions.
 
90 degrees and 90 minutes is the typical requirement
 