broncosfan
Structural
- Jul 29, 2004
- 44
We are designing a large 500000SF+ warehouse. The solid concrete tilt walls are probably going to be 24' wide, 9 1/4" thick, and 40' high. It's in a low seismic area - design category B. The joists (supporting 22GA metal deck)are at approximately 6' o.c. and sit on 8"x6"x12"long ledger angles welded to steel embeds. My question(s) have to do with the chord force. First, in calculating the chord force, it can be shown that each individual 24' wide concrete panel has enough overturning resistance at 0.6D to resist the whole chord force. Does this mean that a connection between the panels at the roof can be eliminated. From talking with a couple other engineers, this actually seems to be fairly common. Second, we plan to run a continuous angle along the wall, welded to the top of the joists with say a 4" fillet weld. Does anybody see a reason that this angle should be attached to the concrete wall as well - say with a fillet weld to another embed on the top leg? Could this extra connection be eliminated if loads are given on the drawings for the joist seats to carry from the bottom of the continuous angle down to the top of the 8"x6" joist seat? Finally, if splices are needed for the continuous angle on the top of the joists (see question 1), should the angle be broken say at the middle of each concrete panel (12' from the joints) so there is a little room to stretch as the concrete shrinks to avoid diagonal shrinkage cracks. WHEW!!! Sorry about the long post. That took longer to type than I thought it would. I'd appreciate any comments.