Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Concrete wall fire resistance

Status
Not open for further replies.

bobby83

Structural
Sep 22, 2014
16
Hello all,
I have a case where the formwork system has tie rods that are removed with the formwork (see image). Cones at both ends of the tie rod are filled with mortar, but it leaves a cylindrical void inside the wall. Does that affect the fire rating of the wall?
635AEFE0-15A3-453B-B08B-D3FC38B54FD7_a0aroh.png
 
Replies continue below

Recommended for you

If so, is there any documentation on this?
 
Normally the entire void is filled with grout (at least in my part of the world. If you don’t do this then i imagine that yes, there is a fire issue - in theory..

Will a fire actually spread through such a small hole? Probably not.. Will anyone stand over that assumption..? Probably not.

Would make an interesting thesis for someone!
 
OP said:
I have a case where the formwork system has tie rods that are removed with the formwork (see image). Cones at both ends of the tie rod are filled with mortar, but it leaves a cylindrical void inside the wall. Does that affect the fire rating of the wall?

I would say that it does not compromise the fire rating given that:

1) flames can't get through.

2) Smoke can't get through.

3) You've surely still got the required cover to your rebar to keep it non-melty.
 
With the appropriate type and depth of patching mortar applied to both sides of the wall the fire rating should be maintained.

See this thread on Hilti Ask: Link
 
No. It does not affect the fire rating. Check any of Gustaferro's publications.

 
Thank you all, have a great week-end!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor