COEngineeer

Structural
Sep 30, 2006
1,186
according to 14.3.5 vertical and horizontal reinforcement shall not be spaced farther apart than 18".

Now usually I spec #5 for basement wall. A lot of time I design it as pinned at the bottom so I need a lot of horizontal reinforcement but not whole lot vertical. Do I still need to use #5 @ 18" o.c. vertically? or can I follow aci 14.2.7? This is ACI 318 btw.

I am asking this because my boss always tell me to put it @ 16" vertical. I feel like for this particular basement wall I design, the horizontal steel will do most of the work (#5 @ 12" o.c.). Can I space the vertical only at 36" o.c.? Based on my calc, 36" o.c. vertical is plentiful. (8" thick wall, d=4).

thanks!

Never, but never question engineer's judgement
 
Replies continue below

Recommended for you

Basement walls can be designed as unreinforced, so you can use whatever spacing you want. But if you exceed the 18" spacing, you must assume the wall is unreinforced.

But I don't understand how you are designing the wall. Basement walls usually span vertically. How are you designing it to span horizontally?

DaveAtkins
 
If you are using reinforcing to carry the load in the horizontal direction, then you have a reinforced wall. You can't have a wall that is reinforced in one direction and unreinforced in the other. So, your maximum bar spacing is 18 inches in both directions. I would go to a #4 bar vertically.
 
dave, I designed it like a tank.

Never, but never question engineer's judgement
 
Then I agree with jmiec--if it's designed as a reinforced structure, use the 18" max spacing.

DaveAtkins
 
k.. i spaced it at 18". I still understand what so significant with 16" o.c. My boss keeps telling me to use 16" o.c. Thanks!

Never, but never question engineer's judgement
 
It's a good practice to use 16" O.C. vertically, as it lines up with increments of block reinforcing.
 