I've got a project that consists of a precast proprietary system with a 2.5" topping slab. As the SER we've design the diaphragm and the precast company designed the precast planks. The plank can span the distance without the topping slab. I've got a request to run up to 5/8"Ø (outside Ø) electrical conduit within the 2.5" slab. I've reviewed ACI and discussed amoungst my office and we're all on the side of not allowing the conduit. ACI requires the conduit to be less that 1/3 of the thickness, so we're ok with that requirement. I also found ACI302.1 requiring 1.5" cover above and below pipes. The slab has welded wire mesh and where the 4 corners of the mesh meet it takes up to 1" of the 2.5". Any thoughts. I've researched online and many forums state they do it all the time with 4" topping slabs which I would agree but with a 2.5" I'm concerned for cracking with such a small section.