We are working on a high rise hotel with a meeting room space hosting more than 300 people; in our opinion, the structure should be categorized as II. FBC 2010 Risk Category Table 1604.5 clearly states that Risk Cat III is meant for 'structures whose primary occupancy is public assembly', in which the hotel is not. IBC 2012 clarifies 'primary occupancy' as 'the portion of the building housing the public assembly occupancy is more than 50% of the total building area' [IBC 2012 pg. 16-10]. We don't think it's logical to punish the whole tower just based on 1 single space of meeting room.
What is your thoughts and experience in this?
Thank you for your input.
What is your thoughts and experience in this?
Thank you for your input.