Please help the electrically simple minded (aka mechanical)

3 phase 240v power...
has 2 conductors.

how do I siphon off 120v regular electricity?
Does 3 phase consist of 2 conductors carrying 120v and one common return line??

Help!! I'm getting more and more confused the more I look at this and try to figure it out.

Any and all responses EXTREMELY appreciated!

schick
 
Replies continue below

Recommended for you

First, I think you are talking about 120/240V single-phase, not three-phase 240V. A three-phase 240V supply would have to have three phase conductors, not two.

The typical residential service (in the U.S.) is 120/240V single phase. There are three wires brought in from the utility. One of the three is a neutral/ground wire. The other two are "hot" wires. The voltage across the two "hot" wires is 240V. The voltage from **either** hot wire to the third (neutral/ground) wire is 120V.

HTH
 

A 3ø source has at least 3 wires. To serve a 1ø 120V load, the simplest way is probably with a 1ø transformer connected to two of three wires.
 
Hi
May be this would be helpful
Your Supply is probably 240 Phase to Phase (basically 2 wires) tapped from a 3 phase source. (I have seen at some locations where 240 V Phase to Phase is generated for specific use to avoid neutral. I presume it may be the same)

You may have to provide transformer to reduce the voltage to 120V but check the voltage across the two wires before proceeding.
 
240v 3Phase is a Delta connection which has a power leg.
There are 2 conductors which measure 120v phase-ground and 240v phase-phase, the power leg will measure 208v phase-ground. You can split off a 120v single phase supply by tapping one of the 120v lines and provide a continuous neutral.
 
Suggestion: The Utility normally installs two overhead transformers in open-delta connection forming the following System Voltage:
Overhead Transformer No. 1:
240V -------------- center tap --------------240V
(No.1 conductor)---(No.2 conductor)---(No.3 conductor)
(120V between each hot conductor 240V and neutral=center tap of one overhead (pole) transformer)
Overhead Transformer No. 2:
240V -------------- center tap --------------240V
(No.4 conductor)---(No.5 conductor)---(No.3 conductor)
(120V between each hot conductor 240V and neutral=center tap of one overhead (pole) transformer)
Remarks:
1. No. 5 conductor may or may not be used in the distribution. It depends.
2. No. 3 conductor of Transformer No. 1 is connected to No. 3 conductor of Transformer No. 2 forming "open delta" three phase, 4-wire system (if conductor No. 5 is not used). It is 240/120V open delta, 3phase, 4wire system.
If conductor No. 5 is used, one obtains 240/120V, 3phase, 5wire system. Average house is usually serviced from one transformer with 240/120V, 1phase, 3wire system.
 