Dear all experts
we are swapping a step-up power transformer of (35MVA 11kv/20kv) that has been defected due to low winding Insulation , but we are facing:
The old Transformer is provided with CT in side the primary winding of the Oil Transformer connected
to relay 87T (SEPAM 2000) but the new swapped transformer isn't provided with this internal C.T.
Proposal to solve the problem :
To connect the primary input of 87T relay( Sepam 2000) to the generator out put CTs in series with generator protection 87G(ALOSTOM) , in this way two protection relays (SEPAM & ALOSTOM) are connecting in series from on CT
what do you think about this connection ?
How can we make functional test (current injection) before charge the Transformer ?
we are swapping a step-up power transformer of (35MVA 11kv/20kv) that has been defected due to low winding Insulation , but we are facing:
The old Transformer is provided with CT in side the primary winding of the Oil Transformer connected
to relay 87T (SEPAM 2000) but the new swapped transformer isn't provided with this internal C.T.
Proposal to solve the problem :
To connect the primary input of 87T relay( Sepam 2000) to the generator out put CTs in series with generator protection 87G(ALOSTOM) , in this way two protection relays (SEPAM & ALOSTOM) are connecting in series from on CT
what do you think about this connection ?
How can we make functional test (current injection) before charge the Transformer ?