19tom56
Marine/Ocean
- Jun 23, 2009
- 6
I have not worked a lot with 1 phase motors, but mainly 3 phase.
Today I had to replace a 1 phase 220 Volt Capasitor start extractor fan motor.
The extractor unit is a radial wheel mounted at the motor shaft.
Everything was connected accoding to the diagram in the lid of the connecting box. Full load is 6.5 Amp. The electromagnetic circuit breaker is a Telemecanic C6 ( 6 amp ) There is no thermal protection in this installation.
First a small test run before the motor and fan was connected to the ducting. It ran 10 seconds, then the breaker tripped.
An investigation showed that the motor wireing coming to the therminal block on motor had been slightly overheated.
A new motor was ordered and a Motorstarter with thermal protection. However thermal motorprotection in a 2 pole version seem to be nonexisting.
Waiting for new parts we decided to install everything again and connect the ventilation duction. Also I reversed the 220 volt Line and Neutral line. The installation drawing states U1 and U2 AC, but not if any are required Line and the other Neutral.
Motor now ran fine, no signs of overheat. Current draw 3 Amp.
The questions are
1. Why did fuse trip and motor wireing overheat.
2. Is it safe to install this motor without a dedicated over current protection. ( There is only a 6 Amp short circuit protection )
3.If electrical diagram is marker U1 and U2, is any supposed to be 220V and the other 0V ( 220 V single phase system )
4. Is there any way you can use a 3 pole 3 phase motorstarter with thermal overload on a 2 pole 1 phase installation.
Regards Torben
Today I had to replace a 1 phase 220 Volt Capasitor start extractor fan motor.
The extractor unit is a radial wheel mounted at the motor shaft.
Everything was connected accoding to the diagram in the lid of the connecting box. Full load is 6.5 Amp. The electromagnetic circuit breaker is a Telemecanic C6 ( 6 amp ) There is no thermal protection in this installation.
First a small test run before the motor and fan was connected to the ducting. It ran 10 seconds, then the breaker tripped.
An investigation showed that the motor wireing coming to the therminal block on motor had been slightly overheated.
A new motor was ordered and a Motorstarter with thermal protection. However thermal motorprotection in a 2 pole version seem to be nonexisting.
Waiting for new parts we decided to install everything again and connect the ventilation duction. Also I reversed the 220 volt Line and Neutral line. The installation drawing states U1 and U2 AC, but not if any are required Line and the other Neutral.
Motor now ran fine, no signs of overheat. Current draw 3 Amp.
The questions are
1. Why did fuse trip and motor wireing overheat.
2. Is it safe to install this motor without a dedicated over current protection. ( There is only a 6 Amp short circuit protection )
3.If electrical diagram is marker U1 and U2, is any supposed to be 220V and the other 0V ( 220 V single phase system )
4. Is there any way you can use a 3 pole 3 phase motorstarter with thermal overload on a 2 pole 1 phase installation.
Regards Torben