Connection of Sprinkler

Status
Not open for further replies.

irfansiddiqui

Industrial
Oct 8, 2012
46
i have a problem in instaling sprinkler.
i have a 4" header then a branch of 1 1/2" and then a branch of 1"
the drop point of sprinkler is out because of unscaling of drawing so i used flexible copper pipe of 1/2" to position of the Sprinkler at the droping point of 1" Pipe.
is it Safe?
is it allowed in NFPA?
 
Replies continue below

Recommended for you

You are not allowed to use 1/2" copper pipe in fire sprinkler systems. The smallest non-ferrous piping to be used is 3/4". The smallest ferrous pipe is 1".

Travis Mack
MFP Design, LLC
 