I have an existing condition that I am trying to work out and make work.
Existing single story light framed house. Roof is 4x10 beams spaced @ 7ft o.c. & 2x T&G spans between. See attached picture of the connection between each 4x10 beam at the ridge point.
Architect wants to install 2x10 framing over the top of the existing 2xt&g & 4x10 beams. The new roof will continue up past the ridge line as a shed roof.
(As you look at the picture roof continues up to the right)
This is only a problem at one location in the house(living room) The actual shear is greater then allowable by about a factor of 2.
In order to make this connection work I was considering two 1/4" thick steel plates, one each side of the 4x10 in order to increase the section modulus for greater shear resistance. Any thoughts? I rough sketched the plate on the picture.
Trying to determine how to analyze this. Could I assume that both steel plates cantilever past the support bolt group on the right beam, therefore creating a moment that has to be distributed through the bolts/beam?
Thanks Erik
Existing single story light framed house. Roof is 4x10 beams spaced @ 7ft o.c. & 2x T&G spans between. See attached picture of the connection between each 4x10 beam at the ridge point.
Architect wants to install 2x10 framing over the top of the existing 2xt&g & 4x10 beams. The new roof will continue up past the ridge line as a shed roof.
(As you look at the picture roof continues up to the right)
This is only a problem at one location in the house(living room) The actual shear is greater then allowable by about a factor of 2.
In order to make this connection work I was considering two 1/4" thick steel plates, one each side of the 4x10 in order to increase the section modulus for greater shear resistance. Any thoughts? I rough sketched the plate on the picture.
Trying to determine how to analyze this. Could I assume that both steel plates cantilever past the support bolt group on the right beam, therefore creating a moment that has to be distributed through the bolts/beam?