sauce_man
Structural
- Apr 14, 2020
- 31
Any insight appreciated.
I have a situation where I need to drop some spandrel beams by 4". This is a podium style application, so these beams are supporting bearing walls above.
Usually I try to maintain 0.5" deflection of spandrel beams due to interactions with façade systems. That plus decent loading makes them nice and deep.
My concern is the connection between floor beams and spandrels.
1. by rule of thumb I like to frame beams at least 1/2 depth of supporting girders (I don't see literature on this)
2. I commonly see min. 3 bolts for spandrel connections (I assume for some kind of moment capacity).
3. I have always seen full depth plate connections for floor beams to spandrels. I assume to prevent torsion, but I cannot find substantial literature on this either.
Do these three points make sense? I am afraid that the by the time my floor beams meet all the above criteria (cope 4", provide three bolts, 1/2 depth of spandrel + 4" drop min beam depth) the client will wonder why infill floor beams with modest spans might be so deep.
Although in most elevated floor cases I have designed the slab edge concrete and edge plates to take façade moment/construction loads, I have always provided "roll beams" perpendicular to spandrels as well. Is this only to provide more torsional robustness?
Thanks in advance,
I have a situation where I need to drop some spandrel beams by 4". This is a podium style application, so these beams are supporting bearing walls above.
Usually I try to maintain 0.5" deflection of spandrel beams due to interactions with façade systems. That plus decent loading makes them nice and deep.
My concern is the connection between floor beams and spandrels.
1. by rule of thumb I like to frame beams at least 1/2 depth of supporting girders (I don't see literature on this)
2. I commonly see min. 3 bolts for spandrel connections (I assume for some kind of moment capacity).
3. I have always seen full depth plate connections for floor beams to spandrels. I assume to prevent torsion, but I cannot find substantial literature on this either.
Do these three points make sense? I am afraid that the by the time my floor beams meet all the above criteria (cope 4", provide three bolts, 1/2 depth of spandrel + 4" drop min beam depth) the client will wonder why infill floor beams with modest spans might be so deep.
Although in most elevated floor cases I have designed the slab edge concrete and edge plates to take façade moment/construction loads, I have always provided "roll beams" perpendicular to spandrels as well. Is this only to provide more torsional robustness?
Thanks in advance,