Conrete FOundation Improvement

Status
Not open for further replies.

StewardMM

Civil/Environmental
Mar 5, 2012
37
We have a distribution Transformer of 2.8 X 1.5m, we will replace it with a new transformer whose base will need to be 3.3 x3 m. we intend to use the existing pad. is it ok to just put some dowel in it and just extend the existing pad?
 
Replies continue below

Recommended for you

If you have to do thatm I would consider encapsulating the old with the new, also using dowels as you suggest as well as a lot of other reinforcing. You may have a problem developing the bottom bars, depending on the loads you have.

Mike McCann
MMC Engineering
 