SoFloJoe
Structural
- Apr 3, 2018
- 76
Hi All,
I am working on a generator pad design. I always used L>2B as my criteria for one way slab vs 2 way. The slab that I am designing has a 43"x76" footprint. This does not meet my normal criteria but I do have a continuous support on the long side on both ends. So there is flexure only in one direction. Per ACI 318-14 7.1.1 it DOES meet the criteria for one way slab as it only flexes in one direction. Would you all agree that this would work under a one way slab condition?
See my attached sketch.
Thanks!
I am working on a generator pad design. I always used L>2B as my criteria for one way slab vs 2 way. The slab that I am designing has a 43"x76" footprint. This does not meet my normal criteria but I do have a continuous support on the long side on both ends. So there is flexure only in one direction. Per ACI 318-14 7.1.1 it DOES meet the criteria for one way slab as it only flexes in one direction. Would you all agree that this would work under a one way slab condition?
See my attached sketch.
Thanks!