basseng
Mechanical
- Jan 27, 2003
- 3
System Description:
2 Trane Centravac 145 Ton chillers in parallel each with a constant flow 290 gpm at 35 ft. head (5 hp) centrifugal chilled water primary pump. 2 variable speed (Danfoss VLT6000 Drives)secondary chilled water pumps (B&G 5x5x9.5 in-line centrigugal)in parallel (1 on standby)with a max. flow of 540 gpm at 45 ft. head (10 hp). Two main loops are 6" diam pipe, and common piping is 6" diam with check valve.
Problem:
When system sees low load and secondary variable flow pumps are operating at low flow, chillers trip out due to low flow conditions (from constant flow primary pumps).
Question:
Does anyone have any idea why the constant flow primary pumps would be operating at lower flow conditions than when the system operates at full load? Can anyone suggest a good reference for design and trouble shooting Constant Primary-Variable Secondary pumping systems?
2 Trane Centravac 145 Ton chillers in parallel each with a constant flow 290 gpm at 35 ft. head (5 hp) centrifugal chilled water primary pump. 2 variable speed (Danfoss VLT6000 Drives)secondary chilled water pumps (B&G 5x5x9.5 in-line centrigugal)in parallel (1 on standby)with a max. flow of 540 gpm at 45 ft. head (10 hp). Two main loops are 6" diam pipe, and common piping is 6" diam with check valve.
Problem:
When system sees low load and secondary variable flow pumps are operating at low flow, chillers trip out due to low flow conditions (from constant flow primary pumps).
Question:
Does anyone have any idea why the constant flow primary pumps would be operating at lower flow conditions than when the system operates at full load? Can anyone suggest a good reference for design and trouble shooting Constant Primary-Variable Secondary pumping systems?