Please refer to the PDF sketch attached.
A construction joint has been constructed that crosses a major concrete transfer beam that we've designed using strut and tie methods. The joint cannot be relocated to a more favourable position.
For a non-STM designed beam, I would address this issue using shear friction provisions. Additionally, I would count on my flexural tension reinforcement to pull double duty as flexural / shear friction steel. If any additional shear friction reinforcement was required, I'd add it to the beam tension steel per ACI recommendations.
Because the girder under consideration was designed using STM methods, I'm wondering if the procedure described in the previous paragraph is still valid. To be consistent with my STM design, I feel that:
1) I should be able to use the horizontal component of the compression strut crossing the joint as an effective clamping force for shear friction computations.
2) I should concentrate any additional reinforcement required for shear friction over the calculated height of the compression strut.
3) I should calculate the maximum permitted shear stress using the vertically projected area of the compression strut rather than the area of the entire beam.
On the one hand, I feel that my shear friction design should be consistent with my STM design, as described above. On the other hand, I feel that the "right" answer should be the same for both STM and sectional design methods.
Please advise.
KootK
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
A construction joint has been constructed that crosses a major concrete transfer beam that we've designed using strut and tie methods. The joint cannot be relocated to a more favourable position.
For a non-STM designed beam, I would address this issue using shear friction provisions. Additionally, I would count on my flexural tension reinforcement to pull double duty as flexural / shear friction steel. If any additional shear friction reinforcement was required, I'd add it to the beam tension steel per ACI recommendations.
Because the girder under consideration was designed using STM methods, I'm wondering if the procedure described in the previous paragraph is still valid. To be consistent with my STM design, I feel that:
1) I should be able to use the horizontal component of the compression strut crossing the joint as an effective clamping force for shear friction computations.
2) I should concentrate any additional reinforcement required for shear friction over the calculated height of the compression strut.
3) I should calculate the maximum permitted shear stress using the vertically projected area of the compression strut rather than the area of the entire beam.
On the one hand, I feel that my shear friction design should be consistent with my STM design, as described above. On the other hand, I feel that the "right" answer should be the same for both STM and sectional design methods.
Please advise.