Hi everyone, I am working on a hoarding design (approx 100m long), and I have to include an access gate in the centre. I am applying Eurocode 1, section 7.4,.1 (free standing walls and parapets)
I was wondering how others deal with the wind load zones (A,B,C,D) at access points. The normal position of the gate is closed (and is the default position during a high wind event) so I would assume that applying zone D wind coefficient was fine. But if anyone out there has any feedback or a different approach I would really like to hear it, particularly any past experience!
I also have a related question that has popped up a few times on the definition of a "return corner"
I was wondering how others deal with the wind load zones (A,B,C,D) at access points. The normal position of the gate is closed (and is the default position during a high wind event) so I would assume that applying zone D wind coefficient was fine. But if anyone out there has any feedback or a different approach I would really like to hear it, particularly any past experience!
I also have a related question that has popped up a few times on the definition of a "return corner"
- The Eurocode illustrates a 90deg corner return, but if we have a 45 deg corner return this should go some way to counter the end effects, but should i handle this.
- Should I treat the 45-degree return as an end since it's less than 90 degrees?
- Or should I interpolate between the "no return corner" coefficients and "return corner" coefficients?