For a project, we have a 2MVA XFMR (4kV/600V) that has a primary feeder protection that consists of a contactor with a 735 Relay and a 300E fuse.
The short circuit rating on the primary side is no more than 4kA. (The application is a waterpump house 2km away fed by a 2MVA XFMR powering some large pumps.)
Looking at a GE 400A 4.16kV Vaccum contactor (Contactor CR193D, I shall paste the ratings at the end of my post.) It says that it is able to withstand 1 second @ 6000A and has a max opening time (max mS) of 50mS
Question: In this schenario (given the 4kA Short Circit) is it possible to use the contactor to open the fault. And can it break the fault in 50mS? (THAT IS FAST.)
Can this be done? I suspicion and I can't find information on contactors being used to open fault conditions and GE's datasheet for the contactor is vague on this regard.
Contactor Ratings:
Source (pg 15-4)
Contactor Ratings—CR193B and CR193D (400A)
Short-time current (amps)
30 seconds 2400
1 second 6000
Impulse withstand (kV) 60
Dielectric strength (kV) 1 minute 18.2
Switching frequency (ops/hour) 360
Mechanical life (ops) 2,000,000
Electrical life (ops) 1,000,000
Closing time (max. ms) 350
Opening time (max. ms)
switched at coil 50
Pick-up voltage (% of rated) 85% max.
Drop out voltage (% of rated) 10%-65%
Control voltage (volts) requires
rectification 110/115 AC
Control circuit burden (VA)
Closing 175
Hold-in 30
Contactor weight 75 lbs. (35 kg)
Standards applicable UL 347
NEMA ICS 3, Part 2
The short circuit rating on the primary side is no more than 4kA. (The application is a waterpump house 2km away fed by a 2MVA XFMR powering some large pumps.)
Looking at a GE 400A 4.16kV Vaccum contactor (Contactor CR193D, I shall paste the ratings at the end of my post.) It says that it is able to withstand 1 second @ 6000A and has a max opening time (max mS) of 50mS
Question: In this schenario (given the 4kA Short Circit) is it possible to use the contactor to open the fault. And can it break the fault in 50mS? (THAT IS FAST.)
Can this be done? I suspicion and I can't find information on contactors being used to open fault conditions and GE's datasheet for the contactor is vague on this regard.
Contactor Ratings:
Source (pg 15-4)
Contactor Ratings—CR193B and CR193D (400A)
Short-time current (amps)
30 seconds 2400
1 second 6000
Impulse withstand (kV) 60
Dielectric strength (kV) 1 minute 18.2
Switching frequency (ops/hour) 360
Mechanical life (ops) 2,000,000
Electrical life (ops) 1,000,000
Closing time (max. ms) 350
Opening time (max. ms)
switched at coil 50
Pick-up voltage (% of rated) 85% max.
Drop out voltage (% of rated) 10%-65%
Control voltage (volts) requires
rectification 110/115 AC
Control circuit burden (VA)
Closing 175
Hold-in 30
Contactor weight 75 lbs. (35 kg)
Standards applicable UL 347
NEMA ICS 3, Part 2