JesperMP
Electrical
- Aug 26, 2003
- 67
Hi,
I would like to hear some of you experts on which method of disengaging a VFD is the best, in particular with respect to E-stop.
1. A contactor in front of the VFD.
Problem is that communication to the VFD will be lost when the contactor is opened (when the VFD control is powered from the mains supply - most are these days).
Also, I have heard that a long waiting time is required before reapplying power (is that really true, does it apply to some or all VFDs ?).
2. A contactor after the VFD.
Problem is that the VFD will experience high voltages on the output terminals if the contactor is opened while the VFD powers the motor.
Some counter this by sending an "inhibit" command to the VFD (from an aux contact on the same contactor), the "inhibit" input is then setup to let the VFD enter cost-to-stop mode thereby avoiding overvoltage alarms. Will this work with any VFD ?
3. No contactor at all.
No problem if no E-stop or safety stop is required (a completely enclosed pump or fan for example).
Some use the VFD to bring the motor to a controlled stop at E-stop.
Problem is that this approach is not allowed in the EU (is it really OK to do so in North America ?).
So, what are you guys doing ?
Are there regulations that has to be followed ?
Thanks for any info
I would like to hear some of you experts on which method of disengaging a VFD is the best, in particular with respect to E-stop.
1. A contactor in front of the VFD.
Problem is that communication to the VFD will be lost when the contactor is opened (when the VFD control is powered from the mains supply - most are these days).
Also, I have heard that a long waiting time is required before reapplying power (is that really true, does it apply to some or all VFDs ?).
2. A contactor after the VFD.
Problem is that the VFD will experience high voltages on the output terminals if the contactor is opened while the VFD powers the motor.
Some counter this by sending an "inhibit" command to the VFD (from an aux contact on the same contactor), the "inhibit" input is then setup to let the VFD enter cost-to-stop mode thereby avoiding overvoltage alarms. Will this work with any VFD ?
3. No contactor at all.
No problem if no E-stop or safety stop is required (a completely enclosed pump or fan for example).
Some use the VFD to bring the motor to a controlled stop at E-stop.
Problem is that this approach is not allowed in the EU (is it really OK to do so in North America ?).
So, what are you guys doing ?
Are there regulations that has to be followed ?
Thanks for any info