itsmoked
Electrical
- Feb 18, 2005
- 19,114
A super heavy grinding machine I'm looking at is to be supplied 220V 3ph (About 115A). Looking into one of its control bays I see every coil for every motor starter and relay are clearly labeled 110 or 120V 60Hz.
There is NO control transformer and all control power is derived from direct connections between the three phases.
How are these coils not toasting? What am I missing? Are the overloads somehow dropping 120V?
Here's the general look:
It's all Allen Bradly stuff from wayyYYYYYYY back.
Keith Cress
kcress -
There is NO control transformer and all control power is derived from direct connections between the three phases.
How are these coils not toasting? What am I missing? Are the overloads somehow dropping 120V?
Here's the general look:
It's all Allen Bradly stuff from wayyYYYYYYY back.
Keith Cress
kcress -