It sounds like the original question was well answered (skin effect)
Jeff – good discussion and I’m glad you responded to my line of discussion regarding interruption.
There is no reason in physics I can come up with that your colleagues would ever suspect loss of interrupting capability at low frequency. Low frequency certainly does not share the unique dc feature of having no current zero's. Can you articulate what possible reservation anyone could have regarding interruption of low frequency current?
In contrast, there is imo strong reason to suspect reduction of interrupting capability as line frequency increases. The basic interrupting mechanism involves a race between recovery of dielectric strength and voltage accross the open contact after interruption. Whenever the actual voltage accross the open contact overtakes the dielectric strength, the arc reestablishes. If this occurs very shortly after reignition during the period of high frequency L-C ringing, it is termed “reignition”. If this occurs more than one quarter cycle after interruption in response to power frequency voltage, it is termed “restrike”. See slide 4 here:
If we compare 60hz to 800hz interruption, there seems no doubt that the dielectric strength recovers at the same rate in both cases, but the power frequency voltage accross the open contact returns faster for 800hz, so it seems inevitable that restrike is more likely at 800hz than at 60hz.
Restrike does not necessarily lead directly to failure to interrupt, but is certainly not a favorable factor for contact life or for successful interuption.
To what extent restrike is a concern for low voltage contactors, and how high frequency would have to get before it becomes a problem, I’m not sure.
=====================================