noel0589
Electrical
- Sep 23, 2004
- 50
Hi all,
If anyone's not tired of this one yet, here is my final question on the matter.
Question: Does anybody know what effects the force at which a contactor will make or break? Why would it close with so much force that it would bounce in one case causing heavy arc damage and close softly in another case under the same starting conditions? Do transients play a role in this?
I have a 200V 50HP AC induction motor operating with an open transition wye-delta starter and 208V power supply.
Our supplier assembles our controllers with starters rated for 40HP, 105A according to the manufacturer. So basically our motor is 50HP, but starter is for 40HP. Normally we have no problems with their starter selection, but in this case we get burning contactors. (We sell elevator systems)
Now, our controller supplier says that it is ok to use a smaller sized reversible contactor in the wye-delta application because of the idea that the current being switched in Delta mode will be a factor of 1/sqrt3. So if the line current of our system at full load runs at 120A,
then Delta contactors will switch at 70A. Since this 70A is well below the rated 105A capacity, our supplier says everything is OK! And it was ok until now.
Actual Observation:
Our delta contacts are burning out. About 1 in every 3 starts it seems like the delta run contacts will "make" or close with so much force that a bouncing effect occurs resulting in heavy arcing damage.
Question Repeated:
Why would delta contacts close with so much force that it would bounce in one case causing heavy arc damage and close softly(normally) on another start under the same starting conditions?
Basically, what affects the force at which a contactor will close?
Would a transient surge in current cause this? Could a surge in current during the wye to delta switch (which is normal in open transition wye delta applications) cause the delta contacts to close with a force that results in bouncing and arcing damage?
Or is it something else completely?
Any suggestions or advice would be appreciated!!
If anyone's not tired of this one yet, here is my final question on the matter.
Question: Does anybody know what effects the force at which a contactor will make or break? Why would it close with so much force that it would bounce in one case causing heavy arc damage and close softly in another case under the same starting conditions? Do transients play a role in this?
I have a 200V 50HP AC induction motor operating with an open transition wye-delta starter and 208V power supply.
Our supplier assembles our controllers with starters rated for 40HP, 105A according to the manufacturer. So basically our motor is 50HP, but starter is for 40HP. Normally we have no problems with their starter selection, but in this case we get burning contactors. (We sell elevator systems)
Now, our controller supplier says that it is ok to use a smaller sized reversible contactor in the wye-delta application because of the idea that the current being switched in Delta mode will be a factor of 1/sqrt3. So if the line current of our system at full load runs at 120A,
then Delta contactors will switch at 70A. Since this 70A is well below the rated 105A capacity, our supplier says everything is OK! And it was ok until now.
Actual Observation:
Our delta contacts are burning out. About 1 in every 3 starts it seems like the delta run contacts will "make" or close with so much force that a bouncing effect occurs resulting in heavy arcing damage.
Question Repeated:
Why would delta contacts close with so much force that it would bounce in one case causing heavy arc damage and close softly(normally) on another start under the same starting conditions?
Basically, what affects the force at which a contactor will close?
Would a transient surge in current cause this? Could a surge in current during the wye to delta switch (which is normal in open transition wye delta applications) cause the delta contacts to close with a force that results in bouncing and arcing damage?
Or is it something else completely?
Any suggestions or advice would be appreciated!!