Much like the OP in the referenced thread, I have had a GC ask to substitute in a Continuous Galvanized Rebar (ASTM A1094) product.
The literature online appears to be very passionate about the success of Continuous Galvanized Rebar (CGR), but it feels somewhat biased. Most articles seem to source from a particular supplier. However, they are still interesting:
Then there is the white paper discussed in the above thread, "Continuously Galvanized Reinforcing Steel":
One of the upshots of this report is the differences in thickness of the zinc.
ASTM A1094 (Continuously Galvanized rebar) - 2 mils zinc thickness specified. Thinner, but is a purer zinc coating than HDG.
ASTM A767 (HDG rebar) - Class 1 coating is 3.0 ounces/ft2 of zinc works out to 5.9 mil coating. Thicker, but the zinc has more iron in it.
I eventually came across a test performed at the University of Waterloo, "Evaluation of the Corrosion Behaviour of Continuously Galvanized Rebar"
This is a corrosion test comparing Continuously Galvanized to HDG rebar.
The Continuously Galvanized Rebar (CGB) did not perform as well as the HDG, for a few reasons: inconsistent coating thickness and presence of aluminum were the big issues.
"As a result, the author recommends to the producer of the bars that thicker and more uniform coating should be added to the CGR, to at least stand a chance to show similar performance as the conventionally hot-dipped galvanized steels."
This is new to me. So, I thought I'd put it out there, see if anybody had any thoughts.
Much like the OP in the referenced thread, I have had a GC ask to substitute in a Continuous Galvanized Rebar (ASTM A1094) product.
The literature online appears to be very passionate about the success of Continuous Galvanized Rebar (CGR), but it feels somewhat biased. Most articles seem to source from a particular supplier. However, they are still interesting:
Then there is the white paper discussed in the above thread, "Continuously Galvanized Reinforcing Steel":
One of the upshots of this report is the differences in thickness of the zinc.
ASTM A1094 (Continuously Galvanized rebar) - 2 mils zinc thickness specified. Thinner, but is a purer zinc coating than HDG.
ASTM A767 (HDG rebar) - Class 1 coating is 3.0 ounces/ft2 of zinc works out to 5.9 mil coating. Thicker, but the zinc has more iron in it.
I eventually came across a test performed at the University of Waterloo, "Evaluation of the Corrosion Behaviour of Continuously Galvanized Rebar"
This is a corrosion test comparing Continuously Galvanized to HDG rebar.
The Continuously Galvanized Rebar (CGB) did not perform as well as the HDG, for a few reasons: inconsistent coating thickness and presence of aluminum were the big issues.
"As a result, the author recommends to the producer of the bars that thicker and more uniform coating should be added to the CGR, to at least stand a chance to show similar performance as the conventionally hot-dipped galvanized steels."
This is new to me. So, I thought I'd put it out there, see if anybody had any thoughts.