The Project:
Building pad for a Reverse Osmosis and Brine Concentrator Water Treatment Plant.
Strip 18” of native soil.
Compact native soil subgrade to 95%
Place +/- 2’ non expansive fill @ 95%
Place wick drain blanket (12” drain rock between two layers of Mirafi 500X)
Install wicks 5’ on center
Place +/- 15’ non expansive fill @ 95%
Place 10’ surcharge @ 85% (native soil)
The Specifications:
Maximum Density: Is the density obtained in laboratory when tested in accordance with ASTM D 1557.
In place density: Is density determined in accordance with ASTM D 1557, or ASTM D 2922 and ASTM D 3017.
Non-Expansive Fill: Shall not contain rocks or lumps larger than 4 inches in the greatest dimension and contain no more than 15 percent larger than 2.5 inches. Non-expansive fill shall be predominately granular, have no environmental contaminants or debris. All structural fill shall consist of “non-expansive” fill. (No plasticity index spec.)
Compaction of Embankments and Roadway Fills:
1) Construct in layers of depths specified above.
2) Compact by rolling with power rollers, tamping rollers, vibrating rollers or pneumatic tire rollers.
3) Moisture Content: Bring each layer to between optimum moisture content and +3 percent of optimum moisture content for maximum density before compaction.
The Fill Material:
Overburden from a local sand mining operation. A silty sand with some clay. 100% passing a #4 sieve 48% passing a #200 sieve.
Multiple curves range between 120pcf @ 13% to 117pcf @ 14%
Moisture is +/- 20% in native state.
The Problem:
We have been unable to achieve more than 90 -92% compaction with material at optimum moisture.
What we’ve tried:
1. Place material in 6” lifts, wheel roll with a Cat 824 rubber tired dozer. 83-85% @ 18% moisture
2. Same as above, add 84” vibratory roller. 85-88%
3. Cat 815 sheep foot and 84” vibratory roller. 88-90% @ 13.5% moisture (different location)
4. Cat 825 sheep foot and 84” vibratory roller. 88-90% @ 20% moisture
5. Move all fill to mixing table and disc to dry.
6. Replace fill in lifts with following methods.
7. Cat 825 sheep foot and 84” vibratory roller. 88-90% @ 13.5% moisture
8. Cat 825 sheep foot and 84” vibratory pad drum roller. 88-90% @ 13.5% moisture
9. Cat 825 sheep foot and wheel roll with loaded Cat 623 scraper. 90-92% @ 13.5% moisture
10. Raygo Pactor and wheel roll with loaded Cat 623 scraper. 90-92% @ 13.5% moisture
11. Three different Geotechnical firms ran curves with consistent results.
12. Three different nuclear gauges with consistent results.
Where we stand:
Native soil compaction reached without difficulty.
The Design Engineer agreed to let the 90-92% pass for the fill under the wick drain blanket but still wants 95% for the rest of the fill. We did get one isolated test to get 95% @10.5% moisture and a couple of 93% tests but nothing consistent.
The dry density numbers are between 106pcf and 109pcf
Density numbers drop off rapidly when optimum moisture is exceeded.
The testing engineer has taken some pity on us and is using his lowest curve.
Between installing the wick drain blanket and installing the wicks we have about three weeks to solve this problem.
Alternate sources of material are not available in this area.
We have only placed about 6000 CY of the 139,000 CY required for this project.
Any advice would be appreciated.
Building pad for a Reverse Osmosis and Brine Concentrator Water Treatment Plant.
Strip 18” of native soil.
Compact native soil subgrade to 95%
Place +/- 2’ non expansive fill @ 95%
Place wick drain blanket (12” drain rock between two layers of Mirafi 500X)
Install wicks 5’ on center
Place +/- 15’ non expansive fill @ 95%
Place 10’ surcharge @ 85% (native soil)
The Specifications:
Maximum Density: Is the density obtained in laboratory when tested in accordance with ASTM D 1557.
In place density: Is density determined in accordance with ASTM D 1557, or ASTM D 2922 and ASTM D 3017.
Non-Expansive Fill: Shall not contain rocks or lumps larger than 4 inches in the greatest dimension and contain no more than 15 percent larger than 2.5 inches. Non-expansive fill shall be predominately granular, have no environmental contaminants or debris. All structural fill shall consist of “non-expansive” fill. (No plasticity index spec.)
Compaction of Embankments and Roadway Fills:
1) Construct in layers of depths specified above.
2) Compact by rolling with power rollers, tamping rollers, vibrating rollers or pneumatic tire rollers.
3) Moisture Content: Bring each layer to between optimum moisture content and +3 percent of optimum moisture content for maximum density before compaction.
The Fill Material:
Overburden from a local sand mining operation. A silty sand with some clay. 100% passing a #4 sieve 48% passing a #200 sieve.
Multiple curves range between 120pcf @ 13% to 117pcf @ 14%
Moisture is +/- 20% in native state.
The Problem:
We have been unable to achieve more than 90 -92% compaction with material at optimum moisture.
What we’ve tried:
1. Place material in 6” lifts, wheel roll with a Cat 824 rubber tired dozer. 83-85% @ 18% moisture
2. Same as above, add 84” vibratory roller. 85-88%
3. Cat 815 sheep foot and 84” vibratory roller. 88-90% @ 13.5% moisture (different location)
4. Cat 825 sheep foot and 84” vibratory roller. 88-90% @ 20% moisture
5. Move all fill to mixing table and disc to dry.
6. Replace fill in lifts with following methods.
7. Cat 825 sheep foot and 84” vibratory roller. 88-90% @ 13.5% moisture
8. Cat 825 sheep foot and 84” vibratory pad drum roller. 88-90% @ 13.5% moisture
9. Cat 825 sheep foot and wheel roll with loaded Cat 623 scraper. 90-92% @ 13.5% moisture
10. Raygo Pactor and wheel roll with loaded Cat 623 scraper. 90-92% @ 13.5% moisture
11. Three different Geotechnical firms ran curves with consistent results.
12. Three different nuclear gauges with consistent results.
Where we stand:
Native soil compaction reached without difficulty.
The Design Engineer agreed to let the 90-92% pass for the fill under the wick drain blanket but still wants 95% for the rest of the fill. We did get one isolated test to get 95% @10.5% moisture and a couple of 93% tests but nothing consistent.
The dry density numbers are between 106pcf and 109pcf
Density numbers drop off rapidly when optimum moisture is exceeded.
The testing engineer has taken some pity on us and is using his lowest curve.
Between installing the wick drain blanket and installing the wicks we have about three weeks to solve this problem.
Alternate sources of material are not available in this area.
We have only placed about 6000 CY of the 139,000 CY required for this project.
Any advice would be appreciated.