KHoff
Structural
- Aug 20, 2013
- 60
A gymnasium addition I designed is currently under construction. The slab on grade in the gym consists of 4" concrete with fiber mesh over a 15 mil vapor barrier and granular fill. In addition, I show sawed control joints at 12 feet on center in both directions. The contractor recommended to omit the control joints under the gym floor to prevent curling. I understand curling can occur at a construction joints, so I specify dowels at construction joints. Should I be that concerned about curling at control joints as well? Should I be more concerned about the random cracking that will occur without joints?