Should control joints be used for monolithic slabs, as with other types of slab construction? If so, would the following general rule apply?:

"The joints should be ¼ of the depth of the slab and no more than 2-3 times (in feet) of the thickness of the concrete (in inches). So 4"concrete should have joints 8-12' apart." (source: concretenetwork.com)

Would appreciate some guidance on this.

Thanks.
 
Replies continue below

Recommended for you

Yep. 0.25*depth is general. The max spacing looks excellent too. I would have said 12 feet max if possible, never more than 15 feet which is what you said basically. I haven't heard that rule before; it looks like good advice.
 
What do you mean by the distinction between "monolithic" slabs and "other types" of slab construction?

Please elaborate a bit on what you mean by monolithic.
 
I agree. 2 1/2 times thickness or 10' is the norm for Portland cement concrete. However, if you are looking for a way to increase the joint spacing, you should look into Type K cement, which doesn't shrink. With Type K concrete joint spacing can be 100' or more.
 