control joints in concrete slabs at poolside patio

Status
Not open for further replies.

jdbpe

Structural
Aug 4, 2005
28
Can I get away with 20 foot spaced control joints in a concrete slab that is 4 inches thick that surrounds an in- ground pool at a country club. The control joint is about 1/4 inch deep. The area is somewhat irregular in shape requiring an unsymmetrical control joint pattern with maximum spacing of 20 feet
 
Replies continue below

Recommended for you

Without rebar (not WWF), I would bet that you would get cracking each way at mid panel.

I would suggest control joints at 8 to 10 feet maximum in accordance with PCA requirements. Panels should be approximately square, not rectangular.
 
I wouldn't skimp on this location, as cracking will be noticed and you will get complaints.
 
jdbpe...ditto to jike and cvg comments.

Also, the control joint depth for a 4-inch slab should be 7/8" - 1", and saw them as soon as possible after placement, but in no case more than 12 hours after placement, preferably sooner.
 
Recommended minimum sawcut depth is 1/4 of the depth of the slab. I prefer 1/3.

I also prefer using a "Sofcut" saw, if available.
 