Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Control joints in 12" SOG 1

Status
Not open for further replies.

cec17

Structural
Oct 24, 2014
40
I have an equipment slab that is fairly large 130' x 20' and 12" thick for traffic reasons. I would like to break up the "long" direction with control joints. However, usually the depth of our control joint sawcut is D/4 (and I have seen D/3).

That would put the saw cut in a 12" slab at 3" or 4" deep which is deeper than our top mat of steel. What have you done about control joints in a 12" slab? Just reinforce to 0.5% and don't install control joints? 12" seems like the cutoff zone, where detailing at control joints comes into play due to top mat depth.
 
Replies continue below

Recommended for you

Thanks dik. I can't recall ever specifying epoxy coated bars and don't plan on it here... I have always heard that if they get any damage onsite, from the usual abuse and toss-around, it can increase chance of corrosion. It's not worth the additional cost in this instance given low exposure to chlorides.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor