I have an equipment slab that is fairly large 130' x 20' and 12" thick for traffic reasons. I would like to break up the "long" direction with control joints. However, usually the depth of our control joint sawcut is D/4 (and I have seen D/3).

That would put the saw cut in a 12" slab at 3" or 4" deep which is deeper than our top mat of steel. What have you done about control joints in a 12" slab? Just reinforce to 0.5% and don't install control joints? 12" seems like the cutoff zone, where detailing at control joints comes into play due to top mat depth.
 
Replies continue below

Recommended for you

Thanks dik. I can't recall ever specifying epoxy coated bars and don't plan on it here... I have always heard that if they get any damage onsite, from the usual abuse and toss-around, it can increase chance of corrosion. It's not worth the additional cost in this instance given low exposure to chlorides.
 